1/2/2015 10:08 PM | |
Joined: 9/16/2013 Last visit: 1/27/2022 Posts: 17 Rating:
|
Hi there, I'm facing a problem with connecting 3 siwarex u modules to s7 300 through ET200M. I used the "Getting started package" for calibration and operation of one module only, I got another modified project for operating more than one module but i always get 0 Kg from both channels in all of modules except the first one only, the first module works properly.
AttachmentS7_Token_example_program.zip (312 Downloads) |
1/6/2015 2:59 PM | |
Posts: 206 Rating:
|
Hello Maysara, the for the calibration are stored on the Siwarex U in DR3 (channel 1) and DR4 (channel 2). To calibrate the Siwarex U you can connect to the Siwarex U with a RS232 cable and do the calibration with Siwatool, see also the quick guide http://support.automation.siemens.com/WW/view/en/37733600. If you use the GettingStarted project http://support.automation.siemens.com/WW/view/en/28391777you have the possibility to access the calibration data by the PLC/Panel. and do the calibration respectively. Regards ABenno |