8/7/2007 12:30 PM | |
Joined: 4/24/2006 Last visit: 11/5/2024 Posts: 8766 Rating: (1170) |
Hello, Here are some answers: 1) Yes, you need original Protool programm, migrate it to a WinCC flexible project. Edit the project and download the new project to panel. You will have to do an OS-update first: see following link: http://support.automation.siemens.com/WW/view/en/19701610 2) You are right, direct connection to panel with PC-adapter isn't possible, see following link: http://support.automation.siemens.com/WW/view/en/23802404 You should use a CPU or Repeater to give the PC-adapter power. 3) When you download a project to panel, everything will be overwritten. If there are some authorisations on the panel, like passwords you will have to save it. (prosave). Or with WinCC flexible you download them again. (I hope I did understand it right) Best regards, Wizard |
8/14/2009 12:23 PM | |
Posts: 2 Rating: (0) |
Hi, I'm trying to backup a TP170B via a USB MPI adaptor with prosave is there a way or do I require Wincc Flexible to be able to do this. Regards Robert |
4/8/2015 3:15 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|