Hello, have you project the panel in the HW-config of the cpu? best regards |
4/12/2011 7:51 PM | |
Posts: 167 Rating: (4) |
hi. |
4/12/2011 10:06 PM | |
Joined: 9/27/2006 Last visit: 10/3/2024 Posts: 12283 Rating: (2685) |
Hello poya_xp; If you have icons in the HWConfig for the HMIs, it means you are trying to set them up as DP-slaves. In Siemens' world, however, operator panels are not DP-slaves, but Profibuis-DP Masters Class 2. They operate peer-to-peer with the PLCs To set them up on Profibus, you must configure them in WinCC Flexible (or ProTool), selecting communication partners (the PLC in your case) and setting network and communication parameters; see startingpage 57 of the following WinCC Flexible manual to gat an idea how this is done: http://support.automation.siemens.com/WW/view/en/18797552 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |