7/8/2021 9:34 AM | |
Joined: 1/9/2019 Last visit: 8/20/2024 Posts: 87 Rating: (10) |
HI, please help me on this problem I had a S7-416 2dp plc (416-2xk02-0ab0) v3.1.3, then I wanted to change my system and order s7-416 3pn/Dp v7 (6es7416-3es07-0ab0) plc. IS IT possible to connect this type of plc to HMI TP270 10"? my HMI's are on profibus is there any difference in PROTOOL configuration between these version of PLC's and lower versions for connecting to this type of touch panel? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/08/2021 13:04:45New subject after splitting |
|
7/10/2021 9:57 AM | |
Joined: 5/28/2008 Last visit: 9/30/2024 Posts: 4515 Rating: (839) |
Hello, If the new CPU will have the same Profibus address and same baud rate, it will work. Because in protool project, there is no HW configuration for the CPU. Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |