4/17/2019 1:22 PM | |
Joined: 12/13/2015 Last visit: 5/7/2024 Posts: 22 Rating: (0) |
hello, I have a machine on our company to program with an S7 200 controller, this machine contains an HMI type OP3, I want to change this op3 by a TP177B DP 6 ", after a study that I made, that and possible, it is right? the sorting of the addresses used on the old HMI will be done manually (address test one by one) There are other methods? also this new HMI (Tp177 b) can communicate with all the different version of the S7200 CPUs? ------------------------------------------------------------------------------------------ |
Last edited by: electrikman at: 4/17/2019 1:24:48 PMLast edited by: Jen_Moderator at: 4/18/2019 8:37:17 AMEdited text for better reading. Last edited by: Jen_Moderator at: 4/18/2019 8:42:50 AMNew subject after splitting |
|
4/18/2019 9:11 AM | |
Joined: 5/28/2008 Last visit: 11/4/2024 Posts: 4516 Rating: (839) |
Hello, Yes. TP177B DP can be connected to S7-200 controller. Please have a look in "Process Coupling / Connection to Controller" section of the technical specification of your screen. https://support.industry.siemens.com/cs/ww/en/pv/6AV6642-0BC01-1AX1/td?dl=en |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |