I have done a project connecting 4 PLCs ( Logo 230 RCE) to TP700 comfort successfully; please inform whether 23 number Logo 230 RCE PLCs can be connected to a single TP 1500 Comfort HMI for acquiring ALARMS and status from all 23 PLCs. I have considered only profinet port of the HMI and PLC. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 07/26/2022 13:14:24New subject after splitting Last edited by: Ahfi at: 07/26/2022 18:29:56 |
|
7/27/2022 12:59 PM | |
Joined: 5/30/2022 Last visit: 11/4/2024 Posts: 591 Rating: (96) |
Hi Ahfi, The maximum number of connections allowed is 8 as you can see in this link of the manual: https://support.industry.siemens.com/cs/ww/en/view/49313233/142798424587 |
If this information really helps, you could use the Rate function. |
|
This contribution was helpful to1 thankful Users |
7/27/2022 9:09 PM | |
Joined: 12/18/2014 Last visit: 11/6/2024 Posts: 34147 Rating: (4254) |
Basic Panels only 4 connections, Comfort panels max. 8 connections.
AttachmentSimatic HMI Anzahl Verbindungen.pdf (430 Downloads) |