5/14/2014 9:37 AM | |
Joined: 11/26/2011 Last visit: 6/29/2023 Posts: 508 Rating: (23) |
Sorry. Please find the right onehere.
|
Last edited by: Madhava at: 5/14/2014 2:07 PM |
|
5/14/2014 10:08 AM | |
Joined: 11/26/2011 Last visit: 6/29/2023 Posts: 508 Rating: (23) |
Hi Ayman, Is it possible to change the address of another OP which is running ?
|
5/14/2014 2:00 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Dear Madhava As has been Correctly pointed out by Ayman Elotaify, the MP will always reset the Profibus address to what has been programmed in the Loaded Project, everytime the project runs. Therefore even if you change the profibus address in the control panel, it will be overwritten when the MP goes to Project "RUN" mode. Just for example, if we set a profibus address in the HMI for downloading the project, once the project is download and "RUN" the manually set address is overwritted by the address ( and other settings ) in the project. In my openion, you have only two options : a) Either get hold of the original project ( Not an Uploaded image ) from the person / company who programmed the HMI, change the profibus address and download to the MP. b) Try to upload the image from the faulty MP. Sometimes this is possible, even if the display has failed but rest of the unit is working. Hope this helps Cheers Navnag |
Last edited by: Navnag at: 5/14/2014 2:04 PMThere is no such thing as the last bug in a program |
|