hi I want to connect 32 cpu 1214 to a tp1200 comfort But I can not connect more than 16, and there will be 17 errors in the connection ------------------------------------------------------------------------------------------ |
Last edited by: Madadi at: 9/10/2018 2:04:09 PMLast edited by: Jen_Moderator at: 9/11/2018 6:38:30 AMNew subject after splitting Last edited by: Madadi at: 9/11/2018 7:37:25 AMhttps://pnap.ir |
|
9/7/2020 2:12 PM | |
Joined: 8/3/2009 Last visit: 11/6/2024 Posts: 14106 Rating: (1767)
|
Hello Madadi A comfort Panel is only made for up to 8 Connections simultaniously: Here a like to the System Limits: https://support.industry.siemens.com/cs/de/en/view/109773506/91274388747 If you have much more PLCs then you have to use a PLC for collecting the Data from other PLCs and connect to the HMI or you use a OPC Server (for Example a Simatic Net OPC Server). Here you can make more connections and use the OPC UA Channel in Comfort Panel for connecting to the OPC Server. Bye Murof |