1/9/2017 5:16 PM | |
Posts: 2 Rating: (0) |
Hi Experts, could you help me? I need a 331-1KF01-0AB0 card but siemens representative sent me 331-1KF02-0AB0. According to the specs there are differences on "Input range (rated values) , currents": on 1KF01 the input resistance is 50ohm but on 1KF02 is 100ohm. I am not a specialist but I believe this difference can affect the readings. I am correct? What should be done to avoid it? Attachment01-02.pdf (206 Downloads) |
1/9/2017 5:19 PM | |||||
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Hello, 1KF02 is the successor of 1KF01 there should be no problem Product Details - Industry Mall - Siemens Great Britain Spare part replacement:The new module will replace the module below and isspare part compatible. This means that a module with order no. -1KF01- can simply be replaced by the new module with order no. -1KF02- without having to change the configuration or the wiring.
|
||||
Last edited by: Ste39 at: 1/9/2017 5:21:21 PMLast edited by: Ste39 at: 1/9/2017 5:23:47 PMLast edited by: Ste39 at: 1/9/2017 5:29:19 PM |
|||||
This contribution was helpful to3 thankful Users |
1/10/2017 6:02 PM | |||||
Posts: 2 Rating: (0) |
Hello I replaced the module on plc and it works perfectly and no configuration was needed. Thanks for your help. |
||||
This contribution was helpful to1 thankful Users |
Follow us on