4/25/2015 2:58 PM | |
Posts: 24 Rating: (0) |
Hello Do you now something about error $551? It is missing in datasheet on OP7/OP17. Maybe because OP don't see controller (i doesn't connect controller)? |
4/25/2015 3:41 PM | |
Joined: 3/28/2015 Last visit: 10/4/2024 Posts: 721 Rating: (213) |
Kindly have a look at this link: https://support.industry.siemens.com/cs/attachments/1145112/Op717_e.pdf Error 551 Cause:An MPI/PPI connection to the PLC cannot be established using the specified station address. Remedy:Check MPI station addresses and wiring. |
Last edited by: Min_Moderator at: 4/27/2015 3:54:34 PMReplace non-permanent link Eng.Mohamed Ibrahim |
|
This contribution was helpful to1 thankful Users |
4/27/2015 8:33 AM | |
Posts: 24 Rating: (0) |
Looks like so.. Thanks for link, in russian OP7/17 instruction missing description of error 551. |
This contribution was helpful to2 thankful Users |
5/9/2016 11:37 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by srkimicic is split to a separate thread with the subject Change language in OP7. Best regards |