1/31/2022 5:18 PM | |
Posts: 1 Rating:
|
Good day. We had a disconnection of the voltage regulation (AVR THYRISIEM® Plus) in an electric generator of the Actucha II nuclear power plant. The fault recorded in the THYRISIEM cabinets was: F60064 F60066 I would need to receive more information about the causes that could cause them. Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/01/2022 08:25:04New subject after splitting |
|
2/2/2022 5:37 PM | |
Joined: 7/7/2010 Last visit: 9/16/2025 Posts: 16106 Rating:
|
Perhaps these links from searching this support site are useful: https://support.industry.siemens.com/tf/ww/en/posts/sinamics-dcm-6ra8075-problem/150665 A link to a manual to a similar system might be of help (since Siemens tends to apply the same fault # to the same type of problem): https://cache.industry.siemens.com/dl/files/243/109478243/att_851774/v1/Listenhandbuch_eng.pdf If you have spare parts on hand (I certainly hope you do for a NUC plant), you might want to swap the entire cabinet with another cabinet. However, if you are allowed to troubleshoot further than cabinet level, the above links may help you identify potential candidate components for swapping. That said, if the firmware in a swapped component is not compatible, or you are not expert at determining that, you may want to contact Siemens Support via Support Request or their direct phone line for your region (my recommendation) before swapping components to see if the problem can be resolved with on-hand spare components.
AttachmentListenhandbuch_eng.pdf (553 Downloads) |
Last edited by: Jen_Moderator at: 02/03/2022 10:13:22Added PDF as an attachment. science guy |
|