5/24/2019 1:32 PM | |
Joined: 2/22/2008 Last visit: 8/6/2024 Posts: 2698 Rating:
|
See attached table to find the right Modbus registers. If the beginning address is 0, then reduce numbers by 1. Regards, Scorp AttachmentModbus Tabelle 1.pdf (381 Downloads) |
This contribution was helpful to
1 thankful Users |
5/24/2019 2:08 PM | |
Posts: 24 Rating:
|
Hi scorp, According to your table , is it okay to fill the I/O table like this ? (see attachement) |
5/24/2019 2:11 PM | |
Joined: 12/18/2014 Last visit: 9/6/2024 Posts: 33708 Rating:
|
Hello tipstn, do you use SIMATIC IOT2020/2040? Then look at the IOT2000 conference as I wrote. That's simplier. |
5/24/2019 5:07 PM | |
Posts: 24 Rating:
|
ixo65, I got your idea. I have an iot2020, I went for the modbus method because I could not install node-red-contrib-s7. I tried several times without a result. |
Follow us on