Joined: 12/25/2016 Last visit: 7/10/2024 Posts: 90 Rating: (0) |
hello! I am trying to connect my LOGO to S7-1200 but it seems there is a problem on communicating between the 2. LOGO! to be the client. Please help me. Here is the error i got. AttachmentPLC_COM.zip (274 Downloads) |
4/24/2021 5:50 AM | |
Joined: 12/18/2014 Last visit: 10/1/2024 Posts: 33857 Rating: (4210)
|
You have not allowed the PUT/GET communication. |
This contribution was helpful to2 thankful Users |
4/24/2021 6:02 AM | |
Joined: 12/18/2014 Last visit: 10/1/2024 Posts: 33857 Rating: (4210)
|
There is also a application example from Siemens: LOGO! - S7 Connection with LOGO! Client and S7-1200/1500 Server |