Joined: 8/27/2019 Last visit: 2/7/2024 Posts: 10 Rating: (0) |
Dear Ixo65, I want to move say Input byte 1 to Analog output1 of logo , for hardwiring to other Plc. Kindly suggest / correct me if i m wrong: Example: Mapping in S7-300 PLC: IB0 move to MB0. Similar mapping in LOGO for input byte IB0 (B001) AM1 then AM1 (B002) AQ1. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/28/2022 05:48:01New subject after splitting |
|
1/27/2022 5:55 PM | |
Joined: 12/18/2014 Last visit: 10/10/2024 Posts: 33927 Rating: (4217)
|
You can't transfer directly a IBx to a AQx. There is also no block for MBx. In the LSC software there is no block to read a IBx, only one bit (Ix). That's the reason why you must use the VM area. And AQx has in his input a maximum of 1000 units. This 0-1000 units converts the module AM2 AQ in 0-10V or 0/4-20mA. AttachmentTransfer_IB0_to_AQ1_0BA8.Standard.zip (407 Downloads) |
1/30/2022 6:08 AM | |
Joined: 8/27/2019 Last visit: 2/7/2024 Posts: 10 Rating: (0) |
Thanks You for support |