6/17/2013 11:57 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating:
|
Hi Raffy, where it is converted into an output current of 4 to 20 mA. |
This contribution was helpful to
1 thankful Users |
6/25/2013 5:48 AM | |
Posts: 93 Rating:
|
Dear Raffy, This is current(2-wire) type analog sensor. It's input and output are on the same cable i.e. when you wire your analog input module to this sensor 24V dc will apply directly to +&- cables and current will flow from module -> +cable -> (sensor internal circuit) -> - cable ->module. and current comming from sensor to module is ditected bu module and processed upon it. Hope you get the answer. |
This contribution was helpful to
1 thankful Users |
5/21/2014 6:38 PM | |
Posts: 202 Rating:
|
Hi There thanks for the catalog could you please explain how exactly this sensor works i.e is works the ssame as 2-wire system followed in PLC analog input modules???
|
5/22/2014 7:33 AM | |
Joined: 5/12/2014 Last visit: 9/9/2020 Posts: 149 Rating:
|
Thank for the catalouge, can i connect it directly to the plc analog module??
|
5/22/2014 11:19 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating:
|
Hello@nkur It 'a current sensor 2-wire (4-20mA) I think that you can connect it directly to a PLC. What type of PC you want to connect? What kind of input card you have? |
5/22/2014 11:22 AM |
|
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating:
|
HelloChetan2490 It 'a current sensor 2-wire (4-20mA) I think that you can connect it directly to a PLC. What type of PLC you want to connect? What kind of input card you have? |
Last edited by: Ste39 at: 5/22/2014 11:23 AM |
|