4/23/2015 8:45 AM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4069) |
Here is a possible solution.
AttachmentPump_runtime_and_volume_metering.zip (199 Downloads) |
Last edited by: ixo65 at: 4/23/2015 8:48:26 AM |
|
4/23/2015 8:50 PM | |
Posts: 2 Rating: (0) |
thanks for the sample program, I have not had time to go through it as of yet.
|
4/23/2015 10:35 PM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4069) |
Tonight is no solution shall be. But tomorrow. |
4/24/2015 5:46 AM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4069) |
Here is the complete solution. The nominal value of the flow rate can be adjusted via the display, individually in microliters, milliliters and liters. Counting is done in 822 microliters per second of pump run time. If the specified target value of the flow rate reached or exceeded, the pump shots down. The calculated flow rate is maintained until a new starting operation is initiated. AttachmentPump_runtime_and_volume_metering_V2.zip (190 Downloads) |
Follow us on