2/11/2011 12:47 PM | |
Posts: 206 Rating:
|
Hello, the one second cycle could be to slow, you should use a faster cycle e.g. 100ms, The ERROR 3 indicates that the OCX version no. in DR39 is wrong or the the is not right connected. The d_OCX_write parameters is usedby the OCX to acknowledge the reception of good data via s_KRYPTO_DATA datat record. If the acknowledgement is not working the Siwarex FTA will not send any walid data and ERROR 3 will abear in the OCX. You have to connect the d_OCX_write parameters like it is done in the S7 example http://support.automation.siemens.com/WW/view/de/25296061 The reason for the ERROR 1might be that the DR35 is not read. Regards abenno |