8/9/2017 3:51 PM | |
Posts: 206 Rating:
|
Hello Midelavari, the new Siwarex U need to be calibrated. The easiest way would be to read the calibration data from the old module and send these data to the new one. To do this you can use the Siwatool software and a Siwatool cable. You connect via RS232 and the Siwatool cable to the old Siwarex U and read all data with menu \Communication\Receive all data, sore the data in a file, the connect to the new module and send the data with \Communication\Send all data. The Siwatool you can find in the configuration package for the Siwarex U, that you can by with the order no. 7MH4950-1AK02. If you can't connect to the old Siwarex U any more you have to do a new calibration of the new one. In the QuickGuide that you find here: https://support.industry.siemens.com/cs/ww/en/view/37733600 the calibration procedure is explained. Regards ABenno |
This contribution was helpful to
1 thankful Users |
8/26/2017 7:27 PM | |
Posts: 2 Rating:
|
Dear ABenno, I had tried to calibrate it but it was not successful. Hopefully your suggestion works perfectly. Thanks a lot Regards
|