6/3/2011 10:27 AM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello Palestine, If your application is a weighfeeder you can use either the: - Siwarex FTC (for belt-scales) OR - BW500 The Siwarex FTC (for belt-scales) has no PID-controller on board. That means you have to use the PID-controller of the S7-PLC to control the flow. The BW500 has an onbord PID-controller to control the flow. Attached the technical data sheets from both modules. Best regards Siwarexi Attachmentweighfeeders_BW500_FTC.pdf (214 Downloads) |
This contribution was helpful to
2 thankful Users |
6/4/2011 12:35 PM | |
Posts: 74 Rating:
|
Hello Ayamn Thank you Ayman for your quick response [schnippschnapp] new question is splitted to Connecting Speed sensor to SIWAREX. Best Regards Ahmad
|
Last edited by: O_Moderator at: 6/6/2011 12:45 PM |
|