Hello swatipatwardhan
It means the CP343-1 LEAN can "serve" (handle and respond to) incoming GET/PUT request that are made to it by a Client.
Unfortunately not. You will need to create a so called unilateral connection (see What differences are there when configuring S7 connections? for more on this) and then use GET/PUT (SFB14/15) in your CPU412. You do in this case NOT touch the CPU315 (apart from making sure that the data areas that you intend toget/put from/to it are available). I hope this helps and have a look at the two threads below which contain additional info. Problem with connection between 315-2 PN/DP and 318-2 DP + CP343-1 Lean how to communicate between CPU315-2DP with CP 343-1 lean and IM151-8 PN/DP CPU |
Cheers |
|
5/3/2013 1:03 PM | |
Joined: 1/10/2011 Last visit: 1/11/2023 Posts: 10 Rating: (0) |
Thank you fritz.I got it |