Hi, yes is possible, but you can only use 1 Routeradress for the PLC, not for both Interfaces. Regards Christoph |
7/28/2020 5:55 AM | |
Joined: 5/12/2006 Last visit: 6/14/2024 Posts: 22263 Rating: (2989) |
why should they use the same router if they are 2 independ sub networks? |
7/28/2020 7:52 AM | |
Joined: 5/12/2006 Last visit: 6/14/2024 Posts: 22263 Rating: (2989) |
Further information about the "User router" setting You have the possibility to configure the use of a router including IP address of the router in the "IP protocol" section of the settings for the PROFINET interface (Ethernet addresses). Observe the following rules if you want to configure a router for the PROFINET interface of an IO controller: ● A PROFINET IO device supports exactly one router, irrespective of the number of interfaces. ● You can configure a router for exactly one PROFINET interface. All IO devices that are assigned to the PROFINET interface adopt the configured router from the IO controller. ● You cannot configure a router for the further PROFINET interfaces of the CPU. The further PROFINET interfaces take on the IP address "0.0.0.0" as the router and pass it on to their IO devices. As of STEP 7 V15, you can configure the use of a router for an IO device. This allows the IO device to communicate with a node outside its own IP subnet, irrespective of the setting of the PROFINET interface of the IO controller. https://support.industry.siemens.com/cs/ww/en/view/86140384 Capter 3.4 ... |