10/17/2023 11:09 AM | |
Joined: 6/20/2017 Last visit: 9/9/2024 Posts: 401 Rating:
|
The sensor power supply must be provided externally (5V is not common). The PLC card can provide only the common 24 V. https://mall.industry.siemens.com/mall/en/en/Catalog/Product/6ES7134-6HB00-0CA1 |
Gustavo Antonio Banchetti Brucatori. |
|
This contribution was helpful to
2 thankful Users |
10/17/2023 11:28 AM | |
Joined: 7/19/2022 Last visit: 9/9/2024 Posts: 382 Rating:
|
Hello MartynSmith, The pin you point out does not provide power, it is simply used to read voltage from the sensor signal. If the sensor has to have a fixed 5V power supply, you must give it from an external source, as Gustavo Banchetti comments. |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |
10/17/2023 11:48 AM | |
Joined: 5/17/2022 Last visit: 4/16/2024 Posts: 8 Rating:
|
Thankyou all, i thought this may be the case, but wanted to check :) |
This contribution was helpful to
1 thankful Users |
Follow us on