7/24/2023 10:45 AM | |
Joined: 9/27/2006 Last visit: 6/3/2024 Posts: 12259 Rating: (2670)
|
Hello Andy; The DataEagle radio transmitters présent yhemselves as "transparent Profibus" link. So your project could very well work, in theory. Your DataEagles requirements will need to be respected, for example the maximum speed they will work at (the Profibus ring must be brought down to that transmission rate) and the number of slaves they allow in the Profibus network. These values depend on the DataEagle model you are using in your project.l https://www.adeptor.no/media/multicase/documents//schildknecht/dataeagle%203000%20-%20datasheet.pdf Additinally, on the OLM side, you will have to tweak the Slot_time parameters of the OLMs to ensure that they are able to work with the DataEagle radios in the ring. https://support.industry.siemens.com/cs/ca/en/view/1995199 You might want to talk to Siemens techs (use a Support Request, the link can be found at the top of this page) and Schildknecht support on the DataEagle side, in order to have official reviews of this topology. Hope this helps, |