Duris_I: Wich are the steps to implement the solution? I Try to comunicate a cm1241 RS-485 with Drive Hitachi L300P (ASCII). Can you help me? Thanks in advance. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/21/2019 06:32:33New subject after splitting |
|
11/21/2019 3:41 AM | |
Joined: 3/28/2010 Last visit: 4/17/2024 Posts: 1029 Rating: (211) |
The Hitachi protocol described in this manual https://www.vfds.com/manuals/hitachi-l300p-manual.pdf is a proprietary protocol, it is NOT MODBUS ASCII or Modbus RTU. |