Hello Sathish; Your S7-1200 CPU supports Proniet communications natively (see the technical data) https://support.industry.siemens.com/cs/pd/255094?pdti=td&lc=en-FR Your Omron CJ2M-CPU31 supports Ethernet/IP: CJ2M-CPU3[] / CPU1[] / MD21[] - OMRON Industrial Automation The serial protocols supported by the Omron add-on modules are not supported by a Siemens PLC. What I suggest is a gateway from Profinet to Ethernet/IP between the 2 CPUs; for example (there are other manufacturers yiu can find on the web): http://www.adfweb.com/home/products/PROFINET_EtherNetIP.asp?language=ENG Hope this helps, |