3/12/2021 8:24 AM | |
Posts: 11 Rating: (0) |
Hi! I have a problem with the communication between LOGO8 and CMR2020 via ethernet. The red LED is on of the CMR module, I think i set everithing up properly. Someone coud check it out? Youtube link attached! LOGO 8 IP: 192.168.0.1 HMI IP: 192.168.0.2 CMR2020 IP 192.168.0.3 Thanks! Sorry for my english! ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 03/12/2021 14:40:56New subject after splitting |
|
3/12/2021 11:03 AM | |
Posts: 11 Rating: (0) |
Thanks for your help! I did the update, but the led is still red. Any other ideas? |
3/12/2021 12:20 PM | |
Joined: 11/8/2016 Last visit: 8/29/2024 Posts: 64 Rating: (9) |
What is printed in the diagbuf? Did you set up secure LOGO 8.3 communication at monitoring? |
3/12/2021 1:30 PM | |
Posts: 11 Rating: (0) |
Works!!! There was a problem with the system time! Thanks a lot! |
9/1/2021 11:00 PM | |
Joined: 9/26/2020 Last visit: 8/24/2022 Posts: 2 Rating: (0) |
Hi, how did you make it work? I have the same problem, I tried to use PC time but it still does not work. |
12/16/2021 4:59 PM | |
Joined: 7/9/2021 Last visit: 9/2/2024 Posts: 1 Rating: (0) |
Activate ethernet comunications in logo confortsoft in logo general settings. I attach a pic. |