12/26/2018 5:18 AM | |
Posts: 1 Rating:
|
How we can transfer and receive data s between two s7 300 plc(both are cpu315-2).?. Here we are connecting the two plc by profibus cable in MPI port only.. Can anyone give me suggestions?.. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/26/2018 12:03:29 PMNew subject after splitting |
|
12/26/2018 3:35 PM | |
Joined: 5/6/2010 Last visit: 6/27/2024 Posts: 1970 Rating:
|
Hello, you can use a S7-communication. Hope this is helpful. regards |
12/26/2018 4:01 PM | |
Joined: 9/27/2006 Last visit: 7/24/2024 Posts: 12270 Rating:
|
Hello narasim; Unfortunately, for S7 Communication (Get/Put) for example), a S7-300 can only act as a server, and only with a CP 342-5 in the CPU racks (you need a client in the application, such as a S7-400 CPU). Which types of connection/protocols do the S7-300/400 CPUs and the CPs support by default? https://support.industry.siemens.com/cs/ww/en/view/24352751 If you need to program data exchanges between 2 CPUs 315-2DP connected with a Profibus cable, it would seem easier to use Profibus master-slave connections. Here is a discussion from a few years back with general explanations on the subject, followed by an example of how to use a S7-400 master with a S7 315-2DP slave (you can use a CPU 315-2DP instead of the S7-400 in the example for your project): Two 315-2DP CPUs Profibus Master-Slave communication DP link between CPU 315-2DP (slave) and S7-400 (master) with STEP 7 V5.3 https://support.industry.siemens.com/cs/ww/en/view/6518822 Hope this helps, Daniel Chartier : |
Follow us on