Have you assigned the PG/PC in Netpro? |
10/4/2017 8:39 AM | |
Posts: 51 Rating: (0) |
ok but How I can connect to CPU without PG/PC station. Does PG/PC station ensure s7 routing? |
10/4/2017 11:47 AM | |
Joined: 10/11/2006 Last visit: 11/14/2024 Posts: 5941 Rating: (816)
|
Hello kucukyesiltepe, By looking on the picture you sent with, it looks like, that the firmware for the drives which are built in is unknown hence not installed in the scout. If this is the case, the firmware for the drives is not installed, then install the SSPs for the drives which are used Start there: https://support.industry.siemens.com/cs/ww/en/ps/14517 |
With best regards, |
|
10/4/2017 1:02 PM | |
Joined: 5/12/2006 Last visit: 11/14/2024 Posts: 22452 Rating: (3030)
|
Hi, i think the found devices are all S7 PLC's, he said that the PC is connected to the MPI Network of the PLC's and the drives are connected to the DP Port of PLC's. So accessible Nodes only see the PLC which can't be identified (no Drive) from Starter/Scout as supported Devicetype. Regards Christoph |
10/4/2017 1:44 PM | |
Posts: 51 Rating: (0) |
Yes, Accessible nodes only see the PLC, I want to see d435 and drives connecting with the others network via profibus or ethernet. I want use S7 routing. |