3/11/2020 10:27 AM | |
Joined: 4/24/2006 Last visit: 5/31/2024 Posts: 8664 Rating: (1154) |
Hello, Are you using a CP343-1 Lean, then it is not possible. Because the Lean card can not be a Profinet IO Controller. See the following link: What differences are there between the Industrial Ethernet CPs of SIMATIC S7-300? Best regards, Wizard |
This contribution was helpful to1 thankful Users |
3/11/2020 11:05 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051)
|
hi emilhumm, CP343-1 lean can´t work as IO-Controller, only as IO-Device. see the technical data: You need a CP343-1 6GK7343-1EX30-0XE0hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
3/11/2020 12:59 PM | |
Joined: 9/14/2017 Last visit: 12/1/2022 Posts: 13 Rating: (0) |
You guys are absolutely right. I have a lean version.. |
3/12/2020 8:29 AM | |
Joined: 7/9/2015 Last visit: 5/29/2024 Posts: 3850 Rating: (564)
|
Hi, for you question exists a FAQ - you only need FC11/FC12 once per CP343-1. How do you program communication blocks FC11 and FC12 for the PROFINET IO controller?Regards, Towome |
|
|