Joined: 9/27/2006 Last visit: 5/23/2024 Posts: 12257 Rating: (2668) |
Hello chandrakant; Simatic net (software drivers for S7 communication processors) offers OPC servers for the different Profibus-DP cards in a PC. So you will need to purchase a CP 5612 A2 or a CP 5621, and the required drivers as desctbed below. Then you will need to create an inter¸face with the software where you want to log the data to act as an OPC client. Have a look at the requirements for OPC on a PC with Profibus-DP: What are the options for connecting a PC station to Industrial Ethernet or PROFIBUS via the SIMATIC NET OPC server? Hope this helps, Daniel Chartier |