This is really what I need, how do I define these slots inside the PLC, I want to see the data I'm receiving from the camera inside the PLC |
7/30/2020 8:28 PM | |
Posts: 7 Rating: (0) |
So like this image, I can use I: 102: 0 this is correct, could you please detail for me
|
7/30/2020 8:42 PM | |
Joined: 3/30/2020 Last visit: 6/13/2024 Posts: 4596 Rating: (953) |
See the web page: Download the Instruction Manual. Chapter 13.6. Specifically page 210 of the slot you are mentioning -- The breakdown of all the pieces of information is given there. I102.2 I103.2 is for example "Trigger Acknowledgement". The flow diagrams is very helpful. |
Last edited by: qwazee at: 07/30/2020 20:47:18Add strike-through. Bit 2 of the IW102 is I103.2 Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|