Hello, I would try the following: - Put the IE/PB in the project (add an extra S7-300 in the manzger, but configured as IE/PG gateway by dropping the IE/PB Link in the window) - connect the IE/PB Link to both networks MPI and Ethetnet - connect the PG/PC - add the PG/PC in the project, define for it an Ethernet port connected to the ethernet network and assign this to S7Online. Compile and download the information to all systems. Your project should look like this example (replace profibus by MPI) http://support.automation.siemens.com/WW/view/en/19257092 Some requirements must be met to have S7 routin: See http://support.automation.siemens.com/WW/view/en/584459 |