2/27/2015 2:57 PM | |
Joined: 9/27/2006 Last visit: 5/22/2024 Posts: 12257 Rating: (2668) |
Hello djap; If you set the command word of the VFD to Stop, and the Speed Reference word to 0, you will not influence the motor when you bypass the VFD, and there should be no effect on the Profibus network. However, if you feel you want to disable the VFD as a Profibusa node, you ciuld use SFC 12, "D_ACT_DP". The following link holds some hints: Enabling a disabled DP slave with SFC 12 'D_ACT_DP' Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
2/28/2015 10:29 AM | |
Joined: 9/12/2013 Last visit: 12/14/2023 Posts: 2 Rating: (0) |
Dear Daniel, Thank you for your reply. This is exactly what I need. Thanks again. Cheers, Djap |
Follow us on