12/17/2019 9:23 AM | |
Joined: 4/6/2017 Last visit: 6/16/2022 Posts: 69 Rating: (1) |
Hello all, I have a big issue trying to connect with an S7-1200 CPU 1214C DC/DC/DC 6ES7 214-1AG40-0XB0. The PLC is a new one, purchased in January 2018, but unused until now, it should not have an IP address. I use TIA V15.1 Update 1. With the same PC I can connect to other S7 1200, Siemens HMI and LOGO! I tried all I imagine to connect but does not work. In the attached file are all steps that I tried. Help me please! Rares Attachmentissue.pdf (41 Downloads) |
12/17/2019 10:44 AM | |
Posts: 1283 Rating: (105) |
May I know what is the ethernet IP address defined in your PC? Did you set it to automatic or assigned some fixed IP address? |
12/17/2019 11:23 AM | |
Joined: 4/6/2017 Last visit: 6/16/2022 Posts: 69 Rating: (1) |
I set fixed IP at my PC: 192.168.0.15 |
12/17/2019 4:57 PM | |
Joined: 8/31/2005 Last visit: 5/21/2024 Posts: 2197 Rating: (326) |
Please first use the the configuration in which you can connect to the another CPU. Use a direct cable connection
Some devices should be shown. (see Pic2.png) Now change the connection to the CPU 1214C and klick again on "Update accessible device". If the CPU not found, it may be damaged. It it's found, open it and double klick on "Online & diagnostics" (see Pic3.png) AttachmentPICs.zip (38 Downloads) |
|
|
This contribution was helpful to1 thankful Users |
12/19/2019 10:31 AM | |
Joined: 4/6/2017 Last visit: 6/16/2022 Posts: 69 Rating: (1) |
Problem is almost solved. Some Ethernet settings. I will come back with details. Rares |
Follow us on