8/13/2010 6:04 PM | |
Joined: 9/27/2006 Last visit: 8/7/2024 Posts: 12273 Rating: (2680) |
Hello sun; Here is a quote from GE concerning the communications setup for the PQM meters: The PQM is always a Modbus slave; it cannot be programmed as a Modbus master. |
8/13/2010 6:10 PM | |
Posts: 152 Rating: (2) |
hello dchartier many thanks for info. now i am sure he is mistaken, thanks cheers sun |
Follow us on