6/25/2014 1:54 PM | |
Posts: 3093 Rating: (323)
|
Hello Koenb, you must set DATA_ADDR = 450001. Regards, Kaulquappe |
This contribution was helpful to1 thankful Users |
6/25/2014 3:11 PM | |
Joined: 6/26/2009 Last visit: 5/14/2024 Posts: 122 Rating: (23) |
Thanks a lot . This is solved now . koenb |
This contribution was helpful to2 thankful Users |
3/20/2015 10:50 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4771 Rating: (123) |
|
7/6/2017 2:54 PM | |
Joined: 6/19/2017 Last visit: 6/3/2024 Posts: 8123 Rating: (165) |
New question published by Jchip is split to a separate thread with the subject Communication between s7-1200 and Diris A40( read address 505xx). Best regards |