Hi kryptonneke! With release FS:04, LOGO! 8 supports the Modbus protocol in Ethernet TCP/IP networks. Can find more info in manual. |
If this Information really helps, you could use the Rate function |
|
10/29/2022 1:41 AM | |
Joined: 12/18/2014 Last visit: 9/15/2024 Posts: 33778 Rating: (4194)
|
Your LOGO! with the order number 6ED1 052-1MD08-0BA8 is the LOGO! 8.2, a LOGO! 0BA8 of the 3rd generation. It's a 12/24 RCE with display. In the hardware selection of LSC you have to select LOGO!8.FS4. See attached history file. X34 means it has the FS:02. The firmware V1.82.02 can be upgraded to V1.82.04 via a mSD card. The firmware update you can download from here: Product information on the firmware update for LOGO! 8 for security Vulnerability CVE-2020-7593This LOGO! can Modbus, both Modbus Server and Modbus Client. If you will exchange data between the LOGO! and a Mobdus device you must create a Modbus connection with LSC, either a Modbus server connection or a Modbus client connection. This depends on whether the LOGO! is the server or the client. If the LOGO! is the server, port 502 is selected by default. Give us more information of the Modbus device that you will use. AttachmentVersions of 0BA8.txt (373 Downloads) |
Last edited by: ixo65 at: 10/29/2022 01:47:04Attachment |
|
10/29/2022 10:27 AM | |
Joined: 12/18/2014 Last visit: 9/15/2024 Posts: 33778 Rating: (4194)
|
node-red-contrib-s7 (node) - Node-RED (nodered.org) |