Presuming you have 6GK7 342-5DA00-0XE0, 86 Bytes is indeed its limit as a DP Slave. In that case, upgrading to a newer 5DA01 or 5DA02 will allow you to use up to 240 Bytes. See also THIS FAQ for more. If 240 Bytes is still not enough, configure the CP342-5 as a DP Master and add two more DP/DP couplers to the system (each one does 244 Bytes).
Don't worry about the configured addresses of each universal module. FC2 "DP_RECV" will transfer the entire input range (starting with IB0) to the DB you nominate (which must be long enough). Suggest you pace yourself through THIS document. |