Hello Arun_EE, if your CP supports PROFINET IO Controller-function (e.g.6GK7443-1EX30-0XE1), you can connect PROFINET IO Devices to CP. |
2/15/2019 7:15 AM | |
Joined: 10/7/2005 Last visit: 6/1/2024 Posts: 3007 Rating: (1049)
|
Don't mean to spoil the party, but we are talking S7-400H system and afaik they do NOT support PROFINET I/O's via CP's (not even with the PN H-CPU's which of course do support it in general via their onboard PN port, see also https://support.industry.siemens.com/cs/ww/de/view/90885106 for more and note the fineprint on page 7). |