5/27/2022 10:45 PM | |
Joined: 9/21/2006 Last visit: 5/25/2023 Posts: 247 Rating: (62) |
I am not an expert on the Moxa device nor the barcode scanner. However, looking at the Moxa manual, it looks likely that you could communicate with the Moxa device using S7-1500 OUC communications blocks and a configured TCP connection on the PLC side and the Moxa device in TCP client mode or TCP server mode. If the Moxa is a TCP server, the PLC should do active connection establishment. If the Moxa is a TCP client, the PLC should be the passive side of the connection. Once the connection is established (using TCON or TRCV_C block), you can use the TRCV or TRCV_C block to receive barcode data at the PLC. See How do you program the TSEND_C and TRCV_C instructions for open user communication over the integrated PROFINET interface of the S7-1200/S7-1500 CPU? for more details on using the Open User Communications blocks in the S7-1500 PLC. |
This contribution was helpful to1 thankful Users |