4/28/2016 12:02 PM | |
Joined: 3/20/2012 Last visit: 6/7/2024 Posts: 118 Rating:
|
Hi, I've got a problem with a simple Modbus RTU (RS485) communication. The Comm_Load block returns no "done" and no "error" but a "status" 16#7000 (I've tried to set it to 0, but it comes backs to 16#7000). So the Modbus Master doesn't start, and i've never seen the leds Tx/Rx light. The hardware configuration is based on a CM Ptp / ET200SP ST Station on a Profinet IO, with a 1513 Cpu. All is ok, i've got no defaut, no diagnostic. I've also tried with a S71214 with a CM 1241 rs485. Got the same issue. The DB Modbus Data is not optimised. I've looked into all the examples found on this site, but never found any differences in code, parameters, data, or configuration... See the screenshots attached. Thanks for your help. Best regards. Olivier. AttachmentScreenShot.zip (926 Downloads) |
This contribution was helpful to
1 thankful Users |
4/29/2016 10:41 AM | |
Joined: 3/20/2012 Last visit: 6/7/2024 Posts: 118 Rating:
|
My TIA Portal is V13 + sp1 +upd6. Best regards. |
5/1/2016 6:03 PM | |
Joined: 4/21/2006 Last visit: 7/5/2024 Posts: 510 Rating:
|
New question published by Roger Echave is split to a separate thread with the subject Modbus RTU: status = 7000. Best regards |
7/14/2016 10:41 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating:
|
New question published by AutoGen_958102 is split to a separate thread with the subject S7-1515-2 PN with RS232 slave, COMM_LOAD will not output. Best regards |