1/20/2018 1:22 AM | |
Joined: 9/27/2006 Last visit: 7/13/2024 Posts: 12268 Rating:
|
Hello monir; Have a look at the following sample program for PUT/GET exchanges between S7-300 CPUs, you should find it enlightening. https://support.industry.siemens.com/cs/ca/en/view/18610307 Hope this helps, Daniel Chartier |
Last edited by: Jen_Moderator at: 1/22/2018 9:50:44 AMInserted right link. |
|
This contribution was helpful to
1 thankful Users |
1/22/2018 7:52 AM | |
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating:
|
HEY that is easy when you use PUT in the local CPU with address p#m0.0 byte 4 , that means you will send the data to remote cpu in area starting m0.0 and counting 4 bytes after that byte 0, byte 1, byte2 ,, byte3 . no need to do anything in the remote cpu just make a variable table and watch the data transfering upon the request in the local cpu S7-1200 to S7-300 Plc Communication see this link may it help to understand the operation regardless of cpu version . regards ahmed hamad |
A lot of potential remains |
|
Follow us on