1/2/2024 6:07 AM | |
Joined: 12/30/2013 Last visit: 7/29/2024 Posts: 87 Rating: (0) |
It is correct for drive, but two wire pressure transmitter. What's connection we can do? |
1/2/2024 12:19 PM | |
Joined: 3/11/2019 Last visit: 8/2/2024 Posts: 1540 Rating: (277) |
Hi,
So the fist problem with the drive dos work in the meantime, but now you have a problem with a pressure transmittder? Did I understand that correctly? If you need an additional analog input for a passive 2-wire transmitter, connect your transmitter as a 2-wire to the channel you would like to use. The connection can be found here: SIMATIC ET 200SP analog input module AI 8xI 2-/4-wire BA-> Connection: Current measurement 2-wire connectionAdapt this connection to the channel you would like to use. regards sancruz |
Feedback appreciated, please rate |
|
1/3/2024 6:52 AM | |
Joined: 3/11/2019 Last visit: 8/2/2024 Posts: 1540 Rating: (277) |
Hi, just do the wiring als already explained. If you have a 2-wire transmitter you do not need to connect any external power supply to the transmitter or analog input itself (besides the power supply for the card itself, but this has nothing to do with the input). SIMATIC ET 200SP analog input module AI 8xI 2-/4-wire BA->Connection: Current measurement 2-wire connection regards sancruz |
Last edited by: sancruz at: 01/03/2024 06:54:15Feedback appreciated, please rate |
|