Hi, Did they remove events from Discrete Alarms in HMI Alarming? V19? ------------------------------------------------------------------------------------------ I'm trying to call up different pages when alarms occur. |
Last edited by: Moderator_Lan at: 08/19/2024 08:39:09New subject after splitting Last edited by: C-ABear at: 08/19/2024 21:37:08 |
|
8/19/2024 8:15 AM | |
Joined: 8/6/2024 Last visit: 11/13/2024 Posts: 12 Rating: (0) |
YES,Discrete Alarm has no event. you need use scheduled tasks. |
This contribution was helpful to1 thankful Users |
8/27/2024 7:30 PM | |
Joined: 1/21/2013 Last visit: 11/14/2024 Posts: 3271 Rating: (508)
|
Hi, Scheduled task is one way to respond to changed alarms, but it has some problems with outgoing alarms. In my opinion it is better to use an alarm subscription. Kind regards |
This contribution was helpful to1 thankful Users |
8/29/2024 3:11 AM | |
Joined: 1/30/2024 Last visit: 11/5/2024 Posts: 2 Rating: (0) |
I am trying to change screen on incoming alarm. Scheduled task does not allow me to do this on events. I will research alarm subscription. Thanks, |
9/6/2024 1:05 PM | |
Joined: 8/3/2009 Last visit: 11/13/2024 Posts: 14165 Rating: (1774)
|
Hello C-ABear The best would be to use a screen hierarchie with a screen that is always open like a header screen or a navigation ... Here you can use at screen loading event your subscription and then the callback functions will work as long as this screen will be loaded in the background. Bye Murof |