(0)| 3/25/2020 2:23 AM | |
Joined: 8/19/2012 Last visit: 11/20/2025 Posts: 129 Rating:
Hi dear . I have VLT 5000 with PPO type 1 so during I replacement to FC302 with MCA101 Card and used same PPO type 1 then It work OK .Start /stop via PLC and also received the set point. But not send the acult speed value. So one expert advice me to use PPO6.so I did that I replaced the PPO type 1 to PP0 type 6.and made some changed in the device specific parameters. 1-auto configuration from disable to enable 2-P915/2 from none .To torque limit motor mode. 3-P915/3 From none to ramp 1 ramp up time. Then download HW configuration only to CPU . no profibus error the three FC302 show online in HW. but no data send /received between PLC master and FC302. Then return the PPO type 1 .the communication it OK and the FQ can run from panel .In auto mode only master not received the acult speed value. Please see the PDF if necessary changes the program . Best regards ------------------------------------------------------------------------------------------ AttachmentFC170.pdf (376 Downloads) |
Last edited by: ENG YCS at: 03/25/2020 02:31:20Last edited by: Jen_Moderator at: 03/25/2020 10:44:59New subject after splitting |
| 3/27/2020 12:31 PM | |
Posts: 8171 Rating:
Closed cause question posted twice. The second thread with the subject Replaced the VLT 5000 via FC302 MCA101 - is it okay? is published within the conference Decentral Peripherie. Best regardsJen_Moderator |