11/29/2009 3:47 AM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello deepak; The following application example from Siemens shows you how to setup a CPU 315-2DP as a slave to a CPU 414-2DP. You can setup exactly the same configuration between 2 CPU 313C-2DP, so you can 8understand the basic mechanism of creating an "intelligent" slave. http://support.automation.siemens.com/WW/view/en/6518822 The basic problem is that you must determine exchange data areas between the master and the slave, aand copy the data you want to transfer (for example, in a DB)to these areas so they are transfered to the master and the slave. Study the example attentively; there is even a program download available so you can see how the setup is done (to use it you will need to change the CPUs used in the program). Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/29/2009 2:35 PM |
|
This contribution was helpful to
1 thankful Users |