2/14/2022 1:23 PM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello Setha; You suspect the PLC's power connection for your loss of hardware configuration, this is a possiblity. Do you think the power supply module is the source of your problem, in which case your first step should be to put in a new unit, or is it the plant power that dipped, caused a brownout and left the CPU without power for a very short period? If that is the case, a 24VDC UPS module would allow the PLC to survive these conditions. Here is a link to Siemens Sitop UPS modules, you could also look at other manufacturers with similar offerings. https://new.siemens.com/global/en/products/automation/power-supply/dc-ups.html Hope this helps, |
Last edited by: dchartier at: 02/14/2022 14:46:45 |
|
2/14/2022 1:59 PM | |
Joined: 8/19/2021 Last visit: 3/3/2022 Posts: 2 Rating:
|
Thanks Daniel, i will check it out. |