8/17/2010 1:48 PM | |
Posts: 11 Rating:
|
Howto teriminate Mag 8000 teriminals in Modbus RS-485 communication to PLC S7-224XP. |
8/17/2010 7:41 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello T Murali; The Operating Instructions manual for the Mag 8000 shows how to connectthe unit to Modbus using RS-485; termination instructions are also available. See the attached document. http://support.automation.siemens.com/WW/view/en/19730095 Hope this helps, Daniel Chartier |
8/18/2010 6:35 AM | |
Posts: 11 Rating:
|
i want terimination in the PLC end. |
8/18/2010 7:30 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Mr. Murali; I hope you realize how imprecise your question was, then. Most of the information you will need on the S7-200 is available in the S7-200 System Manual; there is even a chapter on Modbus networks for the S7-200.: http://support.automation.siemens.com/WW/view/en/1109582 The attached document is extracted from this manual, it shows the Port0/Port1 pinouts on the S7-200 CPUs. This FAQ further discusses connections over Modbus for the S7-200 CPUs: http://support.automation.siemens.com/WW/view/en/27832511 It will show you a connection diagram, stating you need touse pins 3 and 8 on the connectors, plus shield and ground connections. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 8/18/2010 8:58 PMLast edited by: dchartier at: 8/18/2010 7:45 PM |
|