5/13/2024 12:12 PM | |
Joined: 8/3/2009 Last visit: 9/15/2025 Posts: 16409 Rating:
|
Hello cyk1019 It will not help you to go "online" in TIA Portal to the HMI. It has no online diagnostiv interface and you will not see any state of your communication. If you show system alarms then there is also an alarm that indicates if the connection is established or not at the beginning of RT Start. Modbus RTU is only developed for Modicon Modbus PLCs. I do not have experience with Beckhoff so I cannot give any tips here: Have a look at the manual perhaps it helps: https://support.industry.siemens.com/cs/ww/en/view/109813307/77442661899 Bye Murof |
If this Information really helps, you could use the Rate function |
|
5/14/2024 4:37 AM | |
Posts: 3 Rating:
|
Hello, Mr Murof. Error code 220007 (Connection is interrupted) is appeared once HMI is started-up. Thus, now in the midst of troubleshooting, would like to know where the connectivity comes from, either IPC or HMI. Let say, if all the setting of HMI are done accordingly to what the manual stated, any method that can be suggest to check the Modbus connectivity of HMI? Because with the use of ModScan and ModPoll, keep on blinking error 220006 (Connection is established) and error 220007 (Connection is interrupted). I would like to ensure HMI programming is correct and able to read and write to the designated Modbus address before proceed to the next. Thanks and regards, cyk1019 |