8/25/2014 9:45 AM | |
Joined: 3/14/2008 Last visit: 9/8/2025 Posts: 2216 Rating:
|
Hello guys, I found an old thread about missing OS application in the component view. I have here application where this is also the case. Opening project on a other ES does not deliver any problems, so the ES is a problem. I checked the WinCCInstallation docs (RASetup, citamis.str etc.) but I cannot see any problems. I checked SQL server and in the databases section, I see one database which has the mark: (supect) behind it. There is no info at all and completely empty. Does someone know if this could be the problem? A suspect database is bad, according to the help section of sql. What happens if I delete the database? It is on a ES, does simatic manager make a new one? How is this being done. Thxxx |
Last edited by: Oreca at: 8/25/2014 1:53 PMIf I could help you, you can use the RATE button. Thank you. |
|
8/26/2014 1:59 PM | |
Joined: 11/16/2012 Last visit: 8/13/2025 Posts: 228 Rating:
|
Hi Oreca, is this a sporadic error? Does a restart of the ES help? Do you have the same language settings on both ES? Do you have already installed the WinCC V6.0 SP3a HF31? Regards jumo |
8/26/2014 3:11 PM | |
Joined: 3/14/2008 Last visit: 9/8/2025 Posts: 2216 Rating:
|
Hello Jumo, Thx for your reaction: No, OS is gone always, also after restart. There was some days before a redundancy problem of the hard disk, maybe database got corrupted. Lanquage is the same, English, HF is not installed, I checked the manual but no improvements based ona missing OS station. Cant I just delete the database? |
Last edited by: Oreca at: 8/26/2014 3:12 PMIf I could help you, you can use the RATE button. Thank you. |
|
8/29/2014 10:30 AM | |
Joined: 3/14/2008 Last visit: 9/8/2025 Posts: 2216 Rating:
|
Hello Guys, I just figured it out. There was a corrupt database, not from WinCC but from VersionDoc (the software that makes backups of the PCS7 projects and checks changes). I deleted the database as it was not from a project and voila, the OS returned. Note: All projects that were retrieved, were missing the OS. So somehow SQL server says to Simatic Manager: No OS for you, maybe its a fail safe plan or something, but the problem is solved. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
2 thankful Users |
2/20/2025 8:51 AM | |
Joined: 9/9/2015 Last visit: 4/9/2025 Posts: 732 Rating:
|
If you are referring to migration from PCS 7 6.1 SP4 to V9.1, you will need to follow a migration step properly before it will work. For example, you might need to migrate to PCS 7 V7.1 SP3 first, then jump to next version , probably PCS 7 V8 or 9. |
Last edited by: JazTai at: 02/20/2025 08:52:19Please give me 5 stars Rating if my post is helpful for you. :) |
|